Start a Conversation

This post is more than 5 years old

Solved!

Go to Solution

3389

September 13th, 2010 09:00

MDS 9513 and AC power connections

I am looking at Cisco MDS 9500 AC power supply connections. There are two power supplies and each power supply has two AC connections. I am looking at MDS documentation and it's not clear if you need to take two connections from a power supply and plug them in to one PDU or if you take one power connections and connect it to PDU 1 and take second connection and connect it to PDU 2 ?

9513powersupply.jpg

Any idea ?

Thanks

71 Posts

September 13th, 2010 13:00

Switches in the MDS 9000 Family have two redundant power supply slots. The power supplies can be

configured in either redundant or combined mode.

• Redundant mode—Uses the capacity of one power supply only. This is the default mode. In case of

power supply failure, the entire switch has sufficient power available in the system.

• Combined mode—Uses the combined capacity of both power supplies. In case of power supply failure,

the entire switch can be shut down (depends on the power used) causing traffic disruption. This mode

is seldom used, except in cases where the switch has two low power supply capacities but a higher power

usage.

In your case (assuming its a 9513)

• Power supplies (6000W AC)
• Input: 100-240V AC nominal (±10% for full range); 16A maximum; 50-60 Hz nominal (±3 Hz for full range)
• Output: 2900W (100V AC at 16A); 6000W (200V AC at 16A)
In 9513 the typical Power usage:-

Cisco MDS 9513

Ports

Typical (Watts)

Max (Watts)

192-ports

1,397

1,552

384-ports

2,097

2,408

528-ports

2,622

3,050


Thus you have options to choose from various combination of voltage and connectivity.

First you need to decide what voltage are you going to provide. For maximum power you will have to connect it to two 220 volt supplies. The table listed earlier does hold good, and the logic for two connections is when we have a lower voltage power supply. The logic given by hersh holds good. However you may see that the switch would even run with single 220 volt AC connection, which will still provide 2900 watts. Though I would also suggest you to go with the recommendations of connecting both the power connections with same PDU.

71 Posts

September 13th, 2010 11:00

Each Power Supply have two AC connections for redundancy, it will be better if you connect both of them to separate PDUs, just in case if one of them fails.

7 Posts

September 13th, 2010 11:00

You need to connect one to PDU 1 and the other to PDU 2 to avoid a single-point-of-failure.

197 Posts

September 13th, 2010 12:00

I think it is the 2 power supplies that give you the redundancy not the 2 connections to a single power supply. Check out this from the Hardware Installation Guide:

One AC power connection @110 VAC = No output

Two AC power connection @110 VAC = 2900 W output

One AC power connection @ 220 VAC = 2900 W output

One AC power connection @110 VAC and one AC power connection @ 220 VAC = 2900 W output

Two AC power connection @ 220 VAC = 6000 W output

Another note, not a power guy here, but any need to be worried about what phase you are connected to? Assuming you have multiple phases in your DC.

2 Intern

 • 

20.4K Posts

September 13th, 2010 12:00

Hmm..so your advices is different from the other guys. You recommend which config:

config 1:

scenario1.jpg

config 2:

scenario2.jpg

2 Intern

 • 

20.4K Posts

September 13th, 2010 12:00

so in case one PDU fails, it's better to run with both power supplies in "degraded" mode versus one power supply in "optimal"mode and one completely dead ?

197 Posts

September 13th, 2010 12:00

Here is the text below the slide I got that picture from:

"The figure illustrates an incorrect and correct connections sequence to external power distribution units. When configured in redundant mode (default), the wrong connection sequence can leave the switch with only 2900W, which can result in the chassis shutting down line card modules. This would require manual configuration to set combined mode, upon which 5800W power capacity is available. There is no automatic provision to configure combined mode in the event there's a loss of an external power source.

The correct connection sequence provides the full 6000W capacity in the event an external power source fails."

2 Intern

 • 

20.4K Posts

September 13th, 2010 12:00

so if two AC power connection at 220 give me 6000W, but one AC Power connection at 220 only gives me 2900.

So if i have PDU die on me, i am left with two power supplied, each running with one power connection. So each is giving me 2900 for a total of 5800 W, but is not equal to 6000W.  Am i completely off with my calculations ?

197 Posts

September 13th, 2010 12:00

You'll need to determine how much Watts you need for your switch. Let's assume you need 5500W to run all your modules. You would connect 2x220V to each power supply (4 power cables connecting to the chassis), this would give you a total of 6000W available. You would setup your power on the MDS as redundant, which is best practice. So if you lose a whole power supply, the other one as able to keep the entire chassis powered up.

I don't think you would want the power supplies connected to different PDUs in this scenero because if PDU goes bad both power supplies would be knocked down to 2900 W which couldn't power all your modules. Now if you had each power supply connected to it's own PDU you could lose a PDU or power supply and keep everything powered up.

197 Posts

September 13th, 2010 12:00

I recommend config 1 and actually those pictures just reminded me of something. I pulled out my book from the Implementing Cisco Storage Networking class and here is the picture in it (sorry for the quality took it from my phone):

IMG00052.jpeg

71 Posts

September 13th, 2010 13:00

I agree with your suggestion of connecting the power connections with the same PDUs. However would like to make a note here, that in case if you are on single 220 volt supply also the switch would receive the required power:-

Max power requirement = 2622 W to 3050 W (all 528 ports in use).

Power supplied when one 220 Volt connection is there = 220 * 16 = 3520 W {Voltage (in Volts) * Current (in Ampere) = Power (in Watts )}

A 10% variation in this would still remain within the max power requirements.

Thus we can still say that this arrangement also takes care of redundant connection, atleast till the same PDU, though not in all input voltage scenarios.

Thanks for pointing out to connect with the same PDUs.

2 Intern

 • 

20.4K Posts

September 13th, 2010 13:00

hersh ..i see the same thing mentioned here:

http://h20000.www2.hp.com/bizsupport/TechSupport/Document.jsp?lang=en&cc=us&taskId=120&prodSeriesId=1849157&prodTypeId=12169&prodSeriesId=1849157&objectID=c00779045

i am going with default config so "config 1" is for me, unless somebody can think of a scenario where "config 2" and "combined mode" on the MDS is more resilient ?

71 Posts

September 13th, 2010 13:00

If you have multiple phases of power supply available, I would prefer to use different phases for each PDUs and thus each power supply getting power from a different power phase.

71 Posts

September 13th, 2010 13:00

2 Intern

 • 

20.4K Posts

September 13th, 2010 13:00

that would make complete sense to me.

Trey, AbhishekKS  ..do you have any reference material that documents your recommendation ?

I appreciate your assistance guys.

No Events found!

Top