Data Centre issue need to re-patch power cables
hello all
we have a H500 and an A200, plugged into 2 PDU, but we have a data centre UPS issue and I wish to move the power cables into new PDU.
Is this straightforward to do? with our VxRail platform I just moved the cables one at a time. does Isilon support this at all?
thanks in advance
Ozen Zorba
28 Posts
1
February 7th, 2023 05:00
Hi,
Gen6 nodes are structured as pairs in the chassis. Since each node can provide power to its pair, you can move power sources from one PDU to another without power outage.
I presumed your current power zone distribution complying with the best practices, please check this before going ahead.
NotStopIsilonProblems
1 Rookie
1 Rookie
•
30 Posts
0
February 8th, 2023 01:00
thanks for this, yes we have followed this configuration. I will arrange to get them migrated over