R610 alarm reseat DIMM B5

Colocation facility reported this alarm to me.  Before I make a trip over, wanted to verify course of action.  I plan to migrate vms, shut down host, reseat DIMM B5 as per alarm.  If alarm reappears, will move dimm to another slot and see if error follows.  If so, probably bad DIMM.  Haven't worked much with this server.  Does it have onboard memory diagnostics I can run  and how, or do I need to download diagnostics tools and use cd or usb?

5 Practitioner

 • 

274.2K Posts

June 15th, 2017 11:00

Hello.

You will probably need to reseat the DIMM before moving over to another slot. Else, swap memory DIMMs B2&B5 with A2&A5 to confirm faulty on the DIMM or slot. Launch LifeCycle Controller (LCC) to run memory diagnostics. Press F10 during POST to enter LCC.